  1. Hi Paul

    As you had also put through your question on Facebook I assumed you were UK based.

    I used the coms sniffer on a V570 to look at a known working Modbus command, read holding registers 0-31 and then tried to duplicate the message using the Protocol FB. I came across a small snag in that the CRC byte order in wrong, it's back to front.

    The working message is

    01 03 00 00 00 20 44 12

    which the Protocol FB generates as

    01 03 00 00 00 20 12 44

    I cannot see a way to reverse the CRC bytes automatically but as I guess you do not need to have many messages you could work out the CRC using the above method and then hard code it in the Protocol FB. The method for generating the CRC for Modbus appears to be binary, zero forward offset, zero backward offset, CRC-16, 256 (100H), 2 bytes.

    Note that the message is only 8 bytes long including the CRC, the screen shots added by Nouy would look like this for my message, two extra bytes at the front of the message.

    00 01 00 03 00 00 00 20 xx yy

    Hope this helps but if you still have issues them please get back to me.

    Tony

  2. I was recently surprised to discover that you can only define 128 alarms in a V1210 PLC, which I think is somewhat light considering how many IO you can attach and control.

    I see from other forum entries that we can use events and build our own alarms but then you have two systems on one PLC.

    The use of alarms in the UK has risen rapidly over the years as we try not to rely on the programming software to diagnose a problem. It would be really useful if some way could be found to increase the total number available in a future software release.

    Here's hoping.