I have attached the application in question. there are several locations in this application where the floating point convert is used. None appear to be working for me.
thanks
-
the OS currently running is V5.04 (B54). Is there something newer? Where can I find the updated OS?
-
the incrementer counts as expected, but the INV(A+B/n) instruction is not working. I can force any number into the MI variable at B or C position of this instruction and it does not change from the program running. The instruction is not running all the time, but should be at this time.
-
I am using a V120 with some floating point math. to be able to display the floating point on the screen I am using the Inv(A + B/n) command. For some reason, this command is always returning and output of "0"
any ideas?
V120 Float: Convert
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
I was wrong. Current OS version was V5.04 (B41). I updated to V5.04 (B54) and the floating point convert seems to be working.
Can you give me an idea as to which version of the OS I might have trouble with? I have many machines around the world with this same V120 PLC installed. Only recently have we noticed any problems with the floating point math?
Thanks,