Duty cycle and frequency


Recommended Posts

Hjalli Sig is talking about the output frequency (The HSO frequency).

We are not sure how to configure it. After testing by changing HSO frequency and testing it with a different HSO Duty Cycles.

It seems that if I give it the value 90 It behaves like i want, but I don't know why.

Link to comment
Share on other sites

Hello

V 350-35-T2

Im configuring the highspeed output PWM. The Duty cycle i understand, from 0 to 1000 or 0-100% but i dont understand why i need to input the frequency ( is the frequency not constantly changing regarding the speed im trying to maintain!

If you are using the PWM function block with an output then you should not be setting up that ouput in the hardware config as an HSO. The PWM block is meant to modulate a single ouput on and off at the selected cycle time and duty.

If you want the hardware HSO to be cotnrolled by your PID output then all you need to do is link your PID output to your HSO "duty cycle" operand and just select an appropriate frequency.

Link to comment
Share on other sites

If you are using the PWM function block with an output then you should not be setting up that ouput in the hardware config as an HSO. The PWM block is meant to modulate a single ouput on and off at the selected cycle time and duty.

If you want the hardware HSO to be cotnrolled by your PID output then all you need to do is link your PID output to your HSO "duty cycle" operand and just select an appropriate frequency.

The problem is to set the appropriate frequency!

We are trying to control a hydro-turbine that runs on 50-60 Hz, we use a heater tube elements connected to the SSR and the OPLC PID-fb to controle the speed of the turbine to generate max power all the time. when we use the power for other things the PID controler loads the heater tube less to ceep up the speed that is set 55HZ .

The question is! The frequency to the to the elements ( power side of the SSR ) changes from 50-60Hz will that affect the set frequency i seleted on the controler ?

Link to comment
Share on other sites

It won't affect the set frequency selected on the controller.

Generally you will want your PWM frequency to be appreciably slower than the oscillating frequency of the power you are switching. I would not use the hardware HSO for this. I get the impression you are trying to sychronize your switching with the generators cycle, which Is probably beyond the capability of the control. I would recommend you use a Zero-Cross phase angle SCR style swtiching device controlled with an analog signal such as 4-20mA. Then just have the PID block source your analog output as opposed to PWM. You will get much more stable operation. Especially if you get an SCR with a linear input to power relationship.

Link to comment
Share on other sites

After reading the in the PID Tips in the Visilogic helpfile I think we need to set the The HSO frequency value to 4.

In the helpfile is written:

If you use an SSR, you can use a Unitronics PLC that supports a high-speed output. In Hardware Configuration, set the Frequency (F=1/CT) parameter's Power-up Value to 5 to 10Hz ( which is 0.2 -0.1s cycle time). Link the PWM Duty Cycle MI to the CV. Note that in order to activate the output pulses, you must SET the RUN MB linked to the HSO in Hardware Configuration.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...