What is the OS version that the PLC has?
Which UniLogic version are you using?
OS: 1.12.20
Firmware: 1.12.7
-
Hi all,
Advise me for the following issue:
- I have a working application, in which after adding a numeric box or meter on HMI display, compiling and downloading is OK, but after download, appears "HMI internal error".
- Rebooting doesn't help.
- When removing the added element and downloading the application the error dissapears.
The HMI display have about a 75 objects in it.
Is there some limitations of number of HMI objects and variables?
Regards,
Plamen Gugulanov
-
Hi,
Sorry for late reply,
I didn't manage to get the things running on XP, so I install Windows 7 and everything is fine
Regards
-
-
Hello,
Finally, I managed to deal with this problem.
Initially I tried one 8GB usb stick, and then one 4GB stick - negative result.After that, I split the 4GB stick in two partitions. The size of partition that worked for me after several trials is approx. 1.5GB and FAT32 file system.
Regards,
Plamen Gugulanov
- 1
-
Hi all,
Same problem with me.
Panel is USP-104-B10 - we have 2 pieces of them - usb stick is not reckognized, and I can't transfer firmware files. -
SI 64 will only calculate the number of files in the main DT folder. To know when a subfolder is full you will need to implement a counter each time a file is added to any SD card subfolders.
Hi.
Aham, okay.
Meanwhile, i did it in a similar way, that you suggest. I used "Folder report" function with a counter....
Thanks for answer.
Regards
-
Hi there,
I'm using V1040 with SD card, on which i'm storing .udt files.
I want to use SI64 as reference for changing the current sub DT(1-4) folder when it is full.
In the ladder application i'm using SB341 as condition for storing SI64 in a MI, but as result SI64 give me the remaining files in main DT folder, not in current sub DT folder (1-4), which i'm using.Did anyone faced the same problem?
Regards
HMI internal error
in UniLogic Software
Posted
Today I made ugrade to Unilogic 1.13.9 and firmware 1.13.5.
I'll check these days if the same error will appear again.