  1. Hello,

    These days I'm having a problem using modbus to reading pressure data from TROX terminal unit. It is kinda simple idea - 7 slaves (TROX units) and V700 is master and gets all the data. But as I'm conneting modbus though all of them I get error that there is no connection between TROX units. Slaves ID are set properly, cable polarity have been checked too. Maybe there are some other problems that I don't know? Thank you kindly for answers.

  2. 5 minutes ago, Ofir said:

    Hi,

    There is no attachment file here.

    Are you using MODBUS TCP or RTU? 

    You will need to check that the communication settings are properly configured (Baud rate, parity, stop bits etc.. IP address, port)

    Check also the value of the status register that is linked to the MODBUS command - this can tell you if the problem relates to communication , register address, etc..

     

    I'm using MODBUS RTU. The tricky part is that baud rate, parity, stop bits, slave ID and port matches perfectly.

    I will try to check status register using online test.

    One more question - if I'm reading only one register from slave, can I display measured variable on HMI at set time frame? for example every 60 seconds it asks for measurement and refreshes last one.

×
×