  1. Hi Joe

    ..still no success with a direct PC-PLC X-over connection where Win10 ipconfig (ethernet adaptor) = 169.254.17.247,      255.255.0.0,     and no firewall and Project Settings are: V700P3,  169.254.17.150,  TCP,  20256,  V700P3

    From PC  pinging the PLC with 169.254.17.150 returns OK.

    No success when I forced MB2 = 1 from within Visilogic

    Network 5 results in MI20 = 34

    Network 6 results in MI21 = 23

    Hope you can help.

    V700P3v1.1.vlp

  2.           Thanks Aus

    MB56 needs to be either a positive or negative transition contact.  It's sole purpose is to trigger the call, not keep on asking for it all the time, or never ask for it, depending on state.  I think Alex probably meant this, but said toggle which you have taken literally and put in a toggle -(X)-.

              No, MB56 is just an on/off switch on the HMI panel

    Some of your questions relate to basic networking knowledge and I suggest you learn a little more about this from the myriad web sources available.

              I am doing, 'til 4 o'clock every morning :(

    It is also possible that your PC's O/S may be blocking the inward request via it's inbuilt firewall.   What are you using?

             Win7

     

  3.  

    What is an IP address you send ping to?

              Parameter B of the PING FB is 169.254.180.182  (as identified by ipconfig)

    Is this IP inside or outside of your network?

              This is just a direct connection between laptop and PLC only

    How you configured PLC OP, Mask, Gateway?

          Details of TCP/IP INIT are:   IP Address D# 169.254.180.200

                                                                       Subnet Mask   D# 255.255.0.0

                                                                      Default Gateway  D# 192.168.1.1

    Does your network require MAC address registration on DHCP Server and Domain Controller?

              I don't know anything about this.

     

    Thanks

    Rob

     

     

     

     


  4. Hi
    I hope somebody could help with some basic questions and problems with a V700:

    1) When assigning sockets and ports do I have to make any special considerations
    for the connection of Visilogic?

    2) Taking one step at a time I'm successful with direct ethernet PC-PLC uploading and monitoring
    (although this is with straight cable NOT crossover - don't know why!) and I'm able to ping
    the PLC (169.254.180.200) from PC(169.254.180.182) but when I try to ping PLC to PC nothing happens.

    See attachmentsCapture1.PNG.769c33cd975c0d9a37d313995c2e49a6.PNG

    Capture2.PNG.b8f4344db75dd1060eaba03e9a0f7ac1.PNG

     

    Socket 4 is ICMP


    3) Also will any extra FB's need to be added to the example posted June 21 2017:

    https://forum.unitronics.com/topic/4746-condition-to-close-a-socket-on-v700/

    to allow successful downloading of data-tables?

     

    Thanks,

    Rob

     

  5. With Joe's code and an LED & Resistor across the 'Step' pins I could see that the voltage level
    was pulsing correctly.

    There was also a steady 24V across the Enable terminals.

    I tried to control the 'Direction' output (O2) with the original code example but couldn't get this to
    work although it did work when conventionally addressed via ladder logic. I don't know why this is.

    So it must be the motor that's faulty or incorrectly configured - I'll swap it with a 2nd one to see.

    Thanks everyone.

    V430_SDSK2310S.pdf

    Forgot to mention:  Teknic's wire colour codes should be ignored.

  6. Initializing &  Resetting the PLC gives the same results. I reduced the Velocity
    down to 125 which gave a longer time before 'at position' was reached but O0-O3 remained
    at a steady zero on the laptop display.

    Could someone please confirm whether or not I should be able to see the outputs
    changing during F9 Online mode? - just in case these PTO modules somehow control the 
    outputs in a  different manner to the ladder code I'm used to.

  7. .... not too familiar with Unitronics stuff but the code in question is in the Main Routine of the Main Module so I assume it is being called continuously.

    I'm also pretty sure I did a few Initialise and Resets because early on, after a main power off - power on cycle, I had displayed Config Success = FALSE and

    Profile Success = FALSE.    I think these changed after an Initialize & Reset.   But I will double check again tomorrow.

     

     

  8. Well, the wiring checked out ok. A clocking circuit 'conventionally' assigned
    to O0, O2 and (for the hell of it) O6 resulted in their corresponding terminals
    pulsing between 0V & 24V as expected and as indicated in F9 Online mode.

    These outputs could not be seen to be switching like this when the PTO ladder modules
    were used so is there some output assignments I'm missing or jumpers or hardware 
    configuration still to consider?

  9. Hi Folks, 

    I'm trying to control a Teknic's SDSK stepper-type motor with a Vision V430 using its PTO functionality but with no success. I don't know if it's a software or hardware problem. Should it be possible for me to see any of the high speed outputs changing state when viewed in Online Test (F9) mode? Because at the moment everything seems to be dead.

    The bit of code I'm using is based on a Unitronics example which I've tried to adapt for a V430 and I'm using VisiLogic 9.8.65

    If anyone could give suggestions as to what I'm missing here it would be much appreciated.

    Best Regards

    Rob

    PTO Test ' Yair.vlp

×
×