  1. I want the STOP Button to reset the operation of the PLC to start afresh from where it started during START Command which it is NOT achieving except, I use ''SB-24'' in NET 7.  It happens when I use the SB-24 (Initialize and Reset PLC (Set to cause PLC Reset and to Initialize all operands to 0) which is not a good practice.  See the updated file attached.

    Other than this, the sequence goes very well.

    110624.vlp

  2. I didn't get MCR-C-I-I-00-DC (2814508 -Phoenix Contact) which is 4-20mA input to 4-20mA output in the market, so I bought MCR-C-U-I- 4-DC - (2814537- Phoenix contact) which is 0-10V input to 4-20mA. I changed my Analog Output to 0-10V in the Hardware Configuration,  I connected the 0-10V as the input to 2814537 and connected the output from it which is 4-20mA to my I/P Transducer, it worked well. Thanks to everyone.

×
×