i am trying to read an input via modbus tcp from a vision 700 with a vision 700. I succeed in reading MIs but i cant find the right addresing for Inputs. Its confusing.. Can someone tell me the adress if I want to read input 0.
There is a type: Pointer + Operand Offset + MODBUS Offset witch i can not understand. Can someone pls explain?
Thank you.
-
Hello. Noob here need some help.
Is it possible to change values in timers through webserver and save that value? I can change the value but oly for one time countdown.
-
Thanks for your reply. So helpful! thank you.
-
Thank you very much!
-
Hi i try to connect this transmiter https://store.clarksonlab.com/HI8936C.aspx .
it has the following terminal. 1. 20+ vdc 2. com 3. com 4. 4-20ma.
1and 2 is the power supply and 4-20 should go in the analog input. plc and transmiter have the same power supply.
i get no signal. I can measure 4-20 ma between +20 vdc and 4-20 ma at the transmiter.
samba has 37 Ω resistance analog input and this transmiter is max 500 Ω output should i use a 500 Ω resistance connected in series?
thank you in advace!
-
i always get 32767. i set the jumper as follows:
jp1 A
jp2 A
jp3 A
jp4 B
jp5 A
jp6 A
jp7 A
jp8 B
jp9 B
jp10 B
jp11 A
JP12 B
i use a 2 wire current sensor 4-20 mA.
i have connected the + of the sensor to the ps and the - to the analog input 5.
i configured the ai5 for 4-20mA.
Modbus
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
Hello
I am trying to read inputs and outputs via modbus tcp from an other plc. i have succeed in reading iputs or outputs but how can i do that simultaniously?