  1. On 1/7/2020 at 9:35 AM, wynn.c.ni@gmail.com said:

    Thank you both

    I ended up getting the drive to function with the I/O pins of the PLC, and using a different configuration setting for the VFD

    I avoided using RS485 but might need to use it in the future. I'll keep in mind to use equipment from the same suppliers in the future.

    I see, so address 43 is frequency, which controls the speed of the motor

    and 34 is the address for Stop/Run

    I was a bit confused by the syntax, but I see that uni stream subtracts 400001 from the MODBUS address to read from

    Best Regards

    Wynn Ni

     

     

  2. Thank you Joe!

    I am new to the protocol and implantation so my terminology  is off when I made the post above.

    I got off the phone with a Siemens Technician and sort of tried to convey the issue to the best of my understanding.

    I think "echo" means to write from the PLC to the VFD

     

    I would like to read speed of the VFD and read the status of the motor (whether it is on/off).

    I would like to write to the VFD to ramp the speed of the motor to a certain value when the program begins and hold the speed constant

    Just something simple to demonstrate motion and that communication is successful.

     

    Much gratitude, 

    Wynn Ni

     

    HMI.PNG

  3. Hi,

    I'm new to the RS485 communication protocol.

    I am trying to communicate with a Siemens SINAMICS V20 VFD with the Unitronics Unistream PLC ( USP-070-B10)

    The VFD leads to a 3 phase motor

    I set up the baud rate to 9600, data bit to 8, parity list to none, and stop bit to 1

    In addition I set up a remote slave in COM1 of Masters drop down, in MODBUS

    In the slave configuration I made a coil named "motor" that writes to address 40 every 100 ms

    I spoke with a Siemens Technician about the driver settings, and could not find a setting to "ECHO" bits to the driver

    I was told I need to set a transmit telegram

    The is there an FC03 for "read holding register" or a way to "Echo" data to 40,100 (MODBUS)?

    Any sort of references or suggestions for setting up communication?

    Thank you,

    Wynn Ni

     

     

     

    Coils.PNG

    COM.PNG

    FC3 Read Holding Registers.PNG

    Inverter Addresses.PNG

    Mapping Table.PNG

    Registers.PNG

×
×