  1. Serial connection through micro usb cable.

    I downloaded the same program from the same pc to an old hmi V700 that I have in my test bench that is more than 5 years old and is working fine. 
    I believe there’s a conflict between the program version and the o/s of the screen.

    Visilogic version now: 9.9.00

    Program creation version: 9:8:90

    Latest saved version:9:8:96

    O/S version: 4.12 (38)

     

  2. Battery voltage 3.3V

    Download

    Download All&Burn

    Set time and date from pc


    I will try the SB8. 


    In one of the hmi’s that I tried to load the program, update of the O.S was needed but not in the second one. 
    It’s a little bit weird that both of them have the same issue, so I think there’s something wrong with the downloading procedure.

    Do I need the latest version of Visilogic maybe?

  3. I use a bargraph in my project  that is linked to a timer.(TD1)

    I set bargraph's  max value using an MI which has the preset value of (TD1).

    when the timer takes values > 00:05:27  the bargraph does not work at all
    when the timer takes values >00:11:10  it works only for some seconds, 
    when i run the simulation i see at the preset value MI a small value, i think it has to do with the overflow,
    it works only at 0 to +32767
    what operand should i use to fit max time of a timer(99h) ?
     

  4. I also have V700 with snap i /o  v200-18-e3 / 4 xb

     i connect a 3-wire PT-100  and place the input in MI operand (C),   the value i get is about 5370.   I measure the resistance from the PT-100 to 120 Ohms so according to pt-100 table it has to be about 50C(the temperature in my room is 22C,maybe the sensor is not good).
    I divide 5370 with 100(no 10 as mentioned in the last post) so i get 53C. Is that correct?

    
     

     

×
×