Hello,
I'm a complete beginner to the topic so I apologise in advance if my terminology is lacking. I'm trying to create a simple application using an Unitronics HMI+PLC SM70-J-T20. I have created necessary logic for the program to work, but now I'm at the point of trying to send signals initialized within the program to a Moxa E1212 I/O module. From what I have gathered, there is no way of operating on the I/O directly through VisiLogic and the only way of communicating with Moxa is through MODBUS IP and addressing of the I/O. I have set IP of the I/O module as well as the HMI according with my local network based of my computer ethernet card. Unfortunately the SB 150 stays at the value of 0. It may be a total non-sense, but I think this means devices are not connecting. I have attached a snipet of the code that is supposed to connect them to each other. Is my syntax or/and understanding of the topic correct?
Thank you so much for any input!
Connecting SM70-J-T20 to Moxa I/O E1212 module
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
@Flex727 Thank you! Turns out that in fact a change of ports was required for the connection to be made.
@AlexUT What about the warning VisiLogic sends if the SB 168 is not included in the project? Is this something I can freely disregard and forget about?
B.R.