  1. To restart and idle EX-RC1 do the following ( with only a 24v DC PSU connected to it ):

    - With the power off switch all the DIP switches On ( Boot Strap Mode )

    - Power it, it will power up with steady PWR LED and flashing I/O COMM and Bus COMM

    - You can now connect via Prg port 57600 BAUD, Get OPLC information returns Model EX-RC1-BOOT, Hardware A, OS Version 2.00 (20) or similar

    - Power it off, change DIP switch all OFF ( Stop Mode )

    - Power it, it will power up with steady PWR and flashing I/O COMM

    - Get OPLC Information returns Model EX-RC1, Hardware A and OS Version 5.04 (14) or similar

    - Get PLC Status will show Run/Stop = Stop

    - Press the Run button, Get PLC Status will show Run/Stop = Run

    - Power it off, change DIP switches to required address 1 to 60

    - Power it, it will power up with steady PWR and flashing Bus COMM

    Normal function is restored.

    Best regards

    Christoph

×
×