To restart and idle EX-RC1 do the following ( with only a 24v DC PSU connected to it ):
- With the power off switch all the DIP switches On ( Boot Strap Mode )
- Power it, it will power up with steady PWR LED and flashing I/O COMM and Bus COMM
- You can now connect via Prg port 57600 BAUD, Get OPLC information returns Model EX-RC1-BOOT, Hardware A, OS Version 2.00 (20) or similar
- Power it off, change DIP switch all OFF ( Stop Mode )
- Power it, it will power up with steady PWR and flashing I/O COMM
- Get OPLC Information returns Model EX-RC1, Hardware A and OS Version 5.04 (14) or similar
- Get PLC Status will show Run/Stop = Stop
- Press the Run button, Get PLC Status will show Run/Stop = Run
- Power it off, change DIP switches to required address 1 to 60
- Power it, it will power up with steady PWR and flashing Bus COMM
Normal function is restored.
Best regards
Christoph