I recently had an EX-RC1 fail on a piece of equipment I have. I have very little support from the manufacturer, but they thought that just swapping the module would fix the issue. I lost CANbus coms between it and the Vision 1210 hmi/plc.
Well I have CANbus coms back up with the new RC1 module, but the RC1 seems to not be configuring as they thought. It appears it needs a program, or I am having some sort of version conflict.
I do have the program for the 1210 hmi. I do not have anything for the RC1.
On the RC1, I can communicate with it vi serial only when it is in bootloader mode. Once I move it out of that mode I can't communicate with it via serial or CAN.
Like I said, I have very limited support from the manufacturer of the machine, and of course we need this thing producing.
I have a Vision 1210 hmi/plc, multiple io via modbus, and then this one RC1 via CANbus, and it is connected to 4x IO-D16A3-TO16. Those modules just sit there with the RUN light slow blinking.
I've done a lot of reading and tutorials but nothing is working for me. There is one where you export the i/o from the plc project, but that uses unilogic, and my project is built in visilogic (9.5.0) so it isn't a guide i can follow. Also unilogic doesn't support the Vision 1210 hmi/plc.
As far as I can tell, I need a project for the RC1. Is there a way to get that from my main 1210 project? Or what am I missing?
Also, when I uploaded the embedded project from the RC1, and did the HWConfig to add the 4 io modules, when I go to download back onto the RC1 it fails due to compiling issues. It does say the RC1 project was created with an older version of visilogic (7.0) but of course that is not available online to download.