AZ1975 Posted October 9, 2013 Report Posted October 9, 2013 HOW DO I IMPORT HMI DISPLAY FROM V1210 TO V570 WITHOUT GETTING THE RUNTIME ERROR AND CRASHING? (VISILOGIC 9.3.1) THANKS
FireNeck Posted October 10, 2013 Report Posted October 10, 2013 Hi AZ1975, please don't shout, we'll hear you... I found that there are two ways of using HMI built for bigger screens on a smaller screen without crashing: 1. Don't call them - works fine, but I think is not what you used 2. Re-Edit the screens. Means, if there are buttons or frames or anything else that would not be visible on a V570 when using a screen made for V1210, the PLC will definetely crash. You have to rearrange the screen so that everything is visible on a V570 screen. No workaround on that, I'm sorry. Hope that helps FireNeck