ricjar Posted December 3, 2014 Report Share Posted December 3, 2014 Hi everyoned! Please I need Help to do communication between V1201 - Ethernet IP with VFD Danfoss Drive Ethernet IP. Quote Link to comment Share on other sites More sharing options...
Walkerok Posted December 9, 2014 Report Share Posted December 9, 2014 I have taken a quick look at the Danfoss information for Modbus and it looks like the VFD only supports Modbus on an RS485 connection and not a TCP connection. The V1210 can only communicate by using Modbus TCP and not through the more generic TCP/IP communications. Talk to your Danfoss supplier and see if there is a Modbus TCP option that I have missed. Keith Quote Link to comment Share on other sites More sharing options...