I need Help to Communicate V1210 Ethernet TCP/IP with Danfoss Drives Ethernet TCP/IP


Recommended Posts

I have taken a quick look at the Danfoss information for Modbus and it looks like the VFD only supports Modbus on an RS485 connection and not a TCP connection.  The V1210 can only communicate by using Modbus TCP and not through the more generic TCP/IP communications.  Talk to your Danfoss supplier and see if there is a Modbus TCP option that I have missed.

 