V350 PLC PT100 32767 not connected or out of range


Recommended Posts

I am new to Visions PLCs and am working on connecting a 3-wire PT100 sensor to a V350-35-TA24 PLC.

I always receive a reading on my HMI of 32767 weather the sensor is connected or not.

Hardware:

I am confident its wired properly (per the manual).  I tested the sensor on an old PID controller just to make sure the sensor works and it displays the temp properly.  The resistance is roughly 108 Ohms when measured with a multi-meter at room temperature.  I am currently using Analog Input 0, but have also tested it on Analog input 1 with the same result.  I have also triple checked the jumpers and they are set to PT100 per the manual.

The two wires that have continuity are wired to analog input 0.  The other wire is connected to CM.

Visilogic:

I have basically nothing in my ladder and have just enough HMI configured to display  MI 1 as a variable:numeric.  This always results in a value of 32767.  I have the correct hardware selected in the HW Configuration.

Visilogic HW configuration:

Analog input 0 - Type PT100 (Alpha = 0.00385)

No Filter

Op:MI

Addr:1

Initialize during powerup: yes

Any help or pointers in the right direction would be greatly appreciated!  Assume I only have very basic knowledge of the visilogic software and any or its quirks.  I also added the project in case that helps.

Thanks in advance!

 

ABC-1002.vlp

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...