Hi , it's my first post,  sorry if i didn't post at the good place.

I'm working on Visilogics , V700 PLC , and i want to communicate with a VAR to pick up Real Value , i recieve 2 Words of 16 Bits , the first for MSW and second for LSW. this is my parameter's value.

I need to interpret this value , but the function in Visilogics to convert Integer to Real are for FIXED point , not FLOATTING point , it means it doesn't work in my case , so i came here to ask you guys if there is something i can do , to avoid having to dissect my both words into mantisse and exosant , and use a formula.

And if there is no function to do it , can you explain to me how to make it simple with this example:  110,1 parameters give me  17 116 for MSW and 13 107 LSW.

This is my first automatician job (that will make me validate my graduate) and i'm still learning , this is the first time i encounter that case , where i have to do it manually so i really need your help please.

Link to comment
Share on other sites

14 hours ago, Gaylord Williams said:

Hi , it's my first post,  sorry if i didn't post at the good place.

I'm working on Visilogics , V700 PLC , and i want to communicate with a VAR to pick up Real Value , i recieve 2 Words of 16 Bits , the first for MSW and second for LSW. this is my parameter's value.

I need to interpret this value , but the function in Visilogics to convert Integer to Real are for FIXED point , not FLOATTING point , it means it doesn't work in my case , so i came here to ask you guys if there is something i can do , to avoid having to dissect my both words into mantisse and exosant , and use a formula.

And if there is no function to do it , can you explain to me how to make it simple with this example:  110,1 parameters give me  17 116 for MSW and 13 107 LSW.

This is my first automatician job (that will make me validate my graduate) and i'm still learning , this is the first time i encounter that case , where i have to do it manually so i really need your help please.

I answered something like that a couple weegs ago.

https://forum.unitronics.com/topic/9447-conversion-the-value-of-a-ieee-754-floating-point/

If I understood correctly you have 1 32 bit  float stored in 2 16 bit MI, you can use the structure function to "Copy" those 2MI on a 1MF. Being the standar Float type AND assuming byte order is the same it will work, if byte order is different you can use swap bytes before structure

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...