I/O Doupts


Guest venkat

Recommended Posts

Hi sir,

We are using Visilogic (V 570), and we are using I/O Expansion module and some I/O,

We checked the I/0 at power up condition that LED was not glowing. I mean we gave 24v dc to I/Os,

And Run LED of the Module is blinking, then I studied the manual and its mentioned this is a Communication Failure,

After I make a communication, now itself the I/O LED is not glowing and Run LED blinking so tell me the Solution……..as much as possible………..

Link to comment
Share on other sites

Hi,

Does the power Led and the comm led on the EX-A1 are On?

Usually the Run Led is blinking if the hardware configuration does not match to the I/O that physically connected.

First of all did you configure in VisiLogic Hardware configuration the I/O you are using?

Make sure that you configured the I/O the same order as it is physically connected.

After configuration is done download the application to the OPLC.

Note that both the OPLC and the EX-A1 must be connected to the same power supply.

You can also review the EX-A1 manual at: http://www.unitronics.com/Data/Uploads/IO_expansions/EX-A1%2012-24VDC.pdf

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...