Guest venkat Posted December 3, 2010 Report Share Posted December 3, 2010 Hi sir, We are using Visilogic (V 570), and we are using I/O Expansion module and some I/O, We checked the I/0 at power up condition that LED was not glowing. I mean we gave 24v dc to I/Os, And Run LED of the Module is blinking, then I studied the manual and its mentioned this is a Communication Failure, After I make a communication, now itself the I/O LED is not glowing and Run LED blinking so tell me the Solution……..as much as possible……….. Quote Link to comment Share on other sites More sharing options...
Ofir Posted December 6, 2010 Report Share Posted December 6, 2010 Hi, Does the power Led and the comm led on the EX-A1 are On? Usually the Run Led is blinking if the hardware configuration does not match to the I/O that physically connected. First of all did you configure in VisiLogic Hardware configuration the I/O you are using? Make sure that you configured the I/O the same order as it is physically connected. After configuration is done download the application to the OPLC. Note that both the OPLC and the EX-A1 must be connected to the same power supply. You can also review the EX-A1 manual at: http://www.unitronics.com/Data/Uploads/IO_expansions/EX-A1%2012-24VDC.pdf Quote Link to comment Share on other sites More sharing options...