  1. Just to expand on what Emil is saying. Inductive loads like motors require suppressors on the contacts to stop them from arching when they open. Inductive loads also draw high currents (up to 10 times their normal current for motors) when the contacts make. This can weld the contacts together inside the relays. I recommend you use contactors rated for the size motors you are controlling rather the PLC relays directly but this may not be necessary for very small motors.

  2. Thanks for the feedback.

    My system is a Dell Precision M6500 with core i7 & 8GB ram, Windows 7 Ultimate 64bit

    Also have a SSD, not sure if it is relevant but if it was I wouldn't expect different behavior within the VM.

    I am running Kaspersky Internet Security 11.0.1.400. It was the first place I looked when the problem occured. Turning it off had no effect.

    The slowness is sporadic, but once it shows up it never just clears up.

    It is most noticeable when doing communications related activities, and doing File Save/Open types of things.

    It also happens often when selecting different subroutines or HMI screens, or inside the HW configuration.

    If I am just building ladder, I rarely see it when I am actually drawing the logic. Only occasionally when I highlight a new network it will go to sleep for a spell.

    Just FYI, I am running a Lenovo ThinkPad X201, Core i5 M580, 4GB of RAM and a 128GB SSD. Using avast! free anti virus.

    I am using VirtualBox on my work server. Linux host and Windows VM guest so we can run our accounting software. VirtualBox works great and it's free. Not a as feature rich as VMware obviously but you can't beat free. Sorry I can't be of more help.

  3. I am really getting frustrated with the odd behavior of Visilogic under Windows 7 64bit. I am suprised that nobody else has been making noise about it. It would be nice to compare systems with someone who is to help possibly indentify the root cause. Since it works in the VM, I can't justify the expense in time trying to work out the Win7 issue.

    Hi Damian

    I'm running on Windows 7 64bit and had a few crashes with VisiLogic 9.3. Haven't had any trouble with VisiLogic 9.3.1 though, and no slow downs on any version. What anti virus are you using?

  4. Hi,

    I have a SIM card with public static IP which after registration to the provider network I'm able to ping its IP, in other hand I have another SIM card which does not have public static IP and after registration I'm not able to ping the IP address.

    Anyway I belive that this relates to the provider setting. As you mentioned also ping is working on specific port which must be enabled by the provider.

    Indeed if the IP address is linked to MI, the IP made up from 4 consecutive MI's.

    I have a sim in my phone that with the correct APN setting I can ping my phone. If I put this sim in the Enfora and use the same APN I cannot ping the PLC. Hopefully when I've fixed the other issues you have pointed out this will work.

    We have a dynamic IP address and I am using the dyndns service to host services (email etc). I'm going to try and use the DNS Resolver FB to update the IP address before the GPRS Start Call FB. If this doesn't work, I will just SMS the current IP to the PLC before the GPRS Start Call FB. I've got plenty to go on for now. I'll keep you updated on my progress.

    Thanks,

    Justin

  5. Hi,

    First please note that GPRS and SMS cannot work at the same time.

    After using any GPRS functionality, you must activate the SMS CONFIG again to be able receive and send SMS messages.

    Another note is that you must also disable the SMS SCAN while using GPRS.

    Regarding the APN settings:

    This limitations related only to the provider of the SIM card.

    If you will have public static IP address then you will be able also to connect the PLC in listen mode.

    Also when you call from the PLC to the PC, if you do not wish to use port forwarding then your PC must have public static IP address.

    Thanks for the info, this solves some of my issues. Should I be able to ping the PLC with it in listen mode? So far I have not and this not a limitation with the sim. Maybe I need to specify a port?

  6. Well, after a full day of testing I'm giving up on remote access via the GSM modem. I managed to establish a remote connection with the PLC in call mode on Friday but it did not work on Monday (I checked the IP address etc). This mode is not desirable anyway because it will only work if port forwarding is set up in the adsl router.

    I never managed to establish a connection with the PLC in listen mode. Using the correct APN this should have worked but it did not. Using the same sim card in my android phone I could ping the phone from an adsl connection but I could not ping the PLC nor connect to it. I just couldn't get a response from the PLC. I don't know how to use the modem to establish a connection to the internet from my PC to test the modem any further. I imagine some drivers are needed but I couldn't find anything.

    I had another issue where the modem would not receive any SMS messages after a call to the PC was made and after unregistering from the GSM network. It will not work again until the PLC is reset.

    If anyone could shed some light on these issues I will have another go but it isn't looking promising.

  7. Not sure how it works elsewere, but in Australia the network sets the baud rate for dial-in (CSD) GSM connections at 9600baud. Since GSM base stations are only made by a few manufactuers, I presume this is going to be reasonably consistent across the globe.

    I have tried setting the modems to 57600, but it does crash out. I presume the 9600baud GSM link causes timeout and/or buffer problkems with the 57600baud local serial links

    For high data rate the other options are to use a Packet Switched Connection (like GPRS) or use a stand-alone broadband modem with Ethernet (and fit ethernet to the PLC).

    Hi Simon. I'm in New Zealand, so it is likely that we use the same system over here. What is required to set up a Packet Switched Connection? I was trying to avoid the broadband band route because I need the SMS capabilities. Are you able to send SMS with a Packet Switched Connection set up?

  8. I'm having trouble with an Enfora modem. With a baud rate of 9600 it will initialise fine. Anything above this and it fails (SB81 = 1). Using Prepare PLC Side Modem completes successfully at 57600 and from the documentation I've read the V1040 should work with this. I would like to be able to connect remotely but at 9600 it is far to slow to be usable. Hopefully someone can shed some light on this problem for me.

    Thanks in advanced,

    Justin

  9. I have set up a Enfora modem on Com port 1 on the PLC and now I cant connect via the USB port. I get the following message:

    ***http://imageshack.us/photo/my-images/220/comerror.png***

    I am using Com 2 for Modbus so can't use this for the modem. I thought that connecting to the USB port would disable Com 1 and this would be OK.

    Can some please offer advice on how I can use Com 1 and USB but not at the same time. It would be OK if I could enable or disable the modem via an operand.

  10. Keith is correct in what he has said and it sounds like you have taken this on board. You will need 2 solenoid valves (or a double block valve ie. 2 valves in 1 unit) between the gas supply and the burner. Your control valve will then come after these valves. Also it is advisable that your safety devices are hard wired to your burner controller. In this case a separate low level device in the wort boiler that disconnects the power to your burner controller if the level goes low. Hope this helps.

    Justin

  11. I've been drawing all my graphics from scratch using Paint.NET. This is a very good program for this sort of drawing. Using layers you can put together some complex background images that can me modified easily in the future.

    I've found out the hard way that you can't just take an image and scale it down. The low resolution of the HMI means that every pixel counts. You can take and image, scale it to correct resolution in Paint.Net. Then add a new layer and trace over the scaled image with a single pixel pencil or other tools. You can then fill in the outlines with the bucket tool etc. Using this method will give you a sharp image which can easily be filled with different colours to indicate different conditions etc. Just save the file as bitmaps for use in the HMI.

  12. I have a modbus device that I would like to update the time on periodically. The date format is not quite the same as the PLC and I can't work out a simple way of sending the correct values.

    The data structure is detailed below (hopefully it will display correctly). All values are 16bit unsigned integers.

    Address Words Description

    49 1 WEEKDAY

    50 3 YEAR, MONTH, DAY

    53 3 HOUR, MINUTE, SECOND

    My intention was to get the correct values into a vector of XI's and then write them to the modbus device in one operation. It looks simple enough but I can't get the correct YEAR, MONTH, DAY values into consecutive XI's in the correct order.

    There maybe be a better way to do this but I can't figure it out with my limited experience. Hopefully someone here can help me out with this one.

    Thanks in advance,

    Justin

  13. Thanks for all your comments guys.

    I am referring to the flash memory not SD. Power up values are not being used because this would overwrite my set points when power is restored. Set points can only be altered by service personnel that have the password. I'm basically trying to insure that there is a recovery method in place that does not require access to the original program or use of a PC. I also want the set points (a vector MI's) recovered.

    I have been experimenting with tables. I can save the set points to the table and restore from the table. However I have just worked out that the data in the table is not stored in flash, only the structure. I can make the data part of the project, and therefore stored in flash but this prevents me from writing to the table. Is my understanding of this correct? If I try to recover the set points from the table after power up (battery removed) I just get random numbers.

    It looks like I may need to use a SD card instead of flash. This may work out better in the long run but will require more work initially.

  14. Hi Emil

    I am using a V1040. I burned the program to flash with the VisiLogic software. I powered down the controller and removed the battery. I waited 10 minutes and then reinstalled the battery. I then powered the controller up.

    I am assuming that at this point the RAM has been erased and therefore the program is loaded from flash. The program runs but all MI's are 0. I thought that the MI values would have been stored in the flash and there restored with the program. Is a Init performed when the program is loaded? Manually performing an Init has the same effect (resetting all MI's to 0).

    I am testing a worst case scenario here. I don't expect this to happen in the field but I need to know how the controller reacts to this type of failure.

    Thanks for your help.

×
×