  1. On 5/4/2012 at 6:54 PM, NickCivco said:

    Hey all..

    Can anyone give me some insight on how to create a button with a password attached? I cannot seem to make a button with a password, only text password strings. I would like to have a button with an image that goes to a supervisor screen that is password protected.

    Yes, I know I am still a newbie!

    Thanks in Advance.

    Nick

    Can you share us your idea for password

  2. On 11/23/2017 at 5:32 PM, Kikis said:

    Hello,

     

    You don't need to use any special function for reading the temperature.

    In hardware configuration within the software, select PT1000 for the analog channel on which you have connected your RTD and link an MI to it.

    Temperature reading from the sensor is directly stored in this MI.

    You can also apply a filter and switch between Celsius and Fahrenait.

     

    Temperature range for PT1000 is -50° to 400°C  with a resolution of 0.1°C.

    So if your MI reads 254, it will be 25.4°C.

     

    Attached is an example for your reference.

     

     

    PT1000_EXAMPLE.U90

    thank you for your answer.

     

     now i have problem with compare the value from pt1000 and set value.

    i choose xxxx.x format for pt value and xxxxx for set value.

    if i set pt>set value I activate output but when it is set value greater than pt value same reaction output is high , can you help

×
×