nwmatney Posted July 10, 2012 Report Share Posted July 10, 2012 I am trying to get my software set up to recognize a 4-20mA input signal. When I navigate to the hardware configuration panel I am confronted with a dropdown menu which does not contain a 4-20mA analog input signal. Where am I going wrong? Link to comment Share on other sites More sharing options...
Walkerok Posted July 10, 2012 Report Share Posted July 10, 2012 Channels 0 and 1 are not able to be 4-20ma inputs. Only channels 2 and 3 are able to be 4-20ma inputs. The V130-33-RA22 installation instructions and specifications documents on the technical documents part of the web site can help you determin what terminals you need to connect to and what settings are available to you on this model PLC. Keith Link to comment Share on other sites More sharing options...
Gabriel Franco Posted July 11, 2012 Report Share Posted July 11, 2012 Only analog inputs #2 and #3 are current/voltage configurable, by jumpers and software. #0 and #1 are for TC, RTD Link to comment Share on other sites More sharing options...
nwmatney Posted July 11, 2012 Author Report Share Posted July 11, 2012 Thanks guys, I knew I was missing something simple somewhere. Link to comment Share on other sites More sharing options...