I am having trouble connecting to a v350-35-ta24. I have the com settings correct(9600,8,n,1) but for some reason I can't connect and I can't download to an SD cad. Could the PLC be password protected in some way? I am using visilogic 9.4.0 with windows xp. If I try using the SD card the screen tell me password missing. What password?

Any help would be much appreciated.

Thanks, Steve

Link to comment
Share on other sites

Hi Steve,

The default baud rate for the V350 series is actually 115200. I would try bumping it up and try again.

As for the SD password, you will not be able to copy a program from the PLC to the SD card unless you have setup an SD password in the program. This is a secruity measure to project your code. To add an SD password you just need a SD password function block in your ladder (under SD--> Set SD password).

If you any other questions regarding trouble shooting please don't hesitate to contact our technical support team at support@unitronics.com