Is it possible to use the two thermocouple inputs set to ohms with a load cell? I recently discovered they want to hook up two 5000 lb load cells with 350 ohm bridge and 2mv/Volt at rated capacity. Do I have to order a load cell card or can the two thermocouple inputs somehow be used? I have a V350-350-RA22 PLC. My other analog inputs are already used.

Link to comment
Share on other sites

It is possible to use the PT100 inputs to directly read ohms though it is not recommended. The input range is only from 1-320 ohms and will only have 12 bit resolution. You will need to set the jumpers and wire the load cells according to the diagrams within the V350-35-RA22 installation guide. The resolution will be in units of 0.1 ohms and there is a conversion time of 300 ms minimum per channel. Each analog input will require a minimum of 100 ms so if using two analog and two RTD that will be a minimum of 100 + 100 + 300 + 300 = 800 ms minimum conversion time.

It will work to measure ohms but will not be able to use the I/O LC-1 & LC-3 features that include:

  • VisiLogic loadcell function blocks(automatic scaling, net min and max, tare, zero, gross weight, setpoints, and filters)

  • A quicker minimum conversion time (min 6.75 ms if using 2x I/O LC-1's or min 675 ms for 2 loadcells with the I/O LC-3)

  • Accurate resloution (I/O LC-1&LC-3 are 24 bit resolution).

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.