amirm Posted August 22, 2014 Report Share Posted August 22, 2014 I have an application that requires 6 encoder inputs, all of them are 1 channel (1 signal output, not quadrature encoder). Maximum pulse rate is 460Hz, let´s make it 500Hz At this rate, I have a square wave that is 1mS high and 1mS low. On my tests, a V350 can run at 1400 scans/second, which is barely enough to see a high input level on a PLC scan, and a low input level on the next scan. Is there any hardware limitation to keep me from doing this? A low-pass filter? Software debounce? These encoders will be used to measure flow, but not total volume. In other words, I can miss a pulse once in a while, or make CLP run faster by not calling subroutines that are not important during flow measurement, which will take 100mS or 200mS, once or twice a second. After I measure the flow, I call these subroutines again (linearization, table write, SD write, Modbus scan, etc.) Thanks Link to comment Share on other sites More sharing options...
Eyal Koren Posted August 25, 2014 Report Share Posted August 25, 2014 Hi Amirm, As stated in the V350 documentation (available here), the typical response time for a normal digital input is 10ms. Hence for a 500Hz signal you will be able to reach a maximum resolution of sampling every 5 pulses. This calculation doesn't take in consideration the scan time, which will make the system even less accurate. Even if the PLC would response faster, according to the Nyquist–Shannon sampling theorem the perfect reconstruction of a signal is possible when the sampling frequency is greater than twice the maximum frequency of the signal being sampled. Hence the maximum scan time+digital input response should be less than 1/1000Hz, which is less than 1ms. Link to comment Share on other sites More sharing options...
amirm Posted August 25, 2014 Author Report Share Posted August 25, 2014 Thanks, Eyal. About Nyquist, I might be wrong, but I just want to count how many pulses I have over some time. If I cared about aliasing, having the exact frequency, or be able to reproduce the signal, then I´d need a sample rate at least twice the signal frequency. Unfortunately, 10mS response time for digital input makes it impractical. The solution: use relays to multiplex the high-speed inputs. As stated before, I just need to read flow. I can sample flow every 2 minutes, and it changes very little over time. Thank you very much! Link to comment Share on other sites More sharing options...
Eyal Koren Posted August 26, 2014 Report Share Posted August 26, 2014 Thanks, Eyal. About Nyquist, I might be wrong, but I just want to count how many pulses I have over some time. If I cared about aliasing, having the exact frequency, or be able to reproduce the signal, then I´d need a sample rate at least twice the signal frequency. Unfortunately, 10mS response time for digital input makes it impractical. The solution: use relays to multiplex the high-speed inputs. As stated before, I just need to read flow. I can sample flow every 2 minutes, and it changes very little over time. Thank you very much! Aliasing and signal reproduction are irrelevant in your case. however, the (relatively) low sampling rate might cause "skipping" of sampling, resulting in wrong flow reading. Anyway, your solution seems very elegant for your system needs. Link to comment Share on other sites More sharing options...