suthipong Posted May 12, 2015 Report Share Posted May 12, 2015 hello I would edit response timeout in modbus master thank Quote Link to comment Share on other sites More sharing options...
Alexander Posted May 12, 2015 Report Share Posted May 12, 2015 The timeout within UniLogic is automatically set, as often the controller will attempt to reconnect using the pre-determined length of time. Is there a reason that you need to edit these values? Quote Link to comment Share on other sites More sharing options...
suthipong Posted May 16, 2015 Author Report Share Posted May 16, 2015 Thank Alexander I do not see blogs Modbus configuration in UniLogic. Quote Link to comment Share on other sites More sharing options...
Alexander Posted May 18, 2015 Report Share Posted May 18, 2015 Within the Modbus Master configuration, each read/write command is periodically triggered using the period value defined in the configuration. If the period is set to 100ms it should automatically attempt to reconnect and send the command using this value. Is there a reason that it would need to be dynamically changed? There is an optional active bit for each individual command that would allow you to enable/disable commands using any ladder or timers. Quote Link to comment Share on other sites More sharing options...