It's not right to define thhe things such a way. In ordinary PID operation, there must be no need at all for Reset Integral error. Most of local PID controllers have no such functions - and the customers even don't know about that.

Usually PID doesn't need to come to status -4. In any specific system there is a need for investigating the reason and improve the parameters to pevent status -4. Just Reset integral error is not the right soluiton.

Link to comment
Share on other sites

Hi Emil,

you are right, in fact you must know that in the last year i've performed some tens pid with unitronics plc and i have not ever used reset

integral error.

With the current job, second my opinion, there is the possibility to fall in this problem. So i think that may need to use, so i'm

informing on how to use this feature. That's all.

With best regards

Fabio

Link to comment
Share on other sites

I stil think that there is no "constant rules", for sure not the "rules" you define there. It looks a little like "maybe I'll go ill someday - which medicine I need to take then?!". I prefer ot stay healthy and - in case of problem, to investigate the reasons and find specific soluitons.

In short - I don't agree with the rules you define to reset Integral error. In case you have problems withh PID - let me know what the problem is and I'll addvice.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...