Once again, I ran into a roadblock where the manufacturer's tech support people couldn't tell me the necessary parameters to set up the EIP communications with a Unistream. They could only direct me to an EDS file online.

With past experience, the EDS file print out, and some trial and error I found the following parameters to work:

Input Assembly Instance: 100, size 24

Output Assembly instance: 150, size 10

Configuration Assembly Instance : 5, size 0

Check the box for "Use Run Idle for O2T" on the Output Assembly Instance

For the Creators: Is there any plan to eventually be able to install EDS files through Unilogic? This would greatly speed up the development time.