Dave Posted May 25, 2018 Report Share Posted May 25, 2018 Once again, I ran into a roadblock where the manufacturer's tech support people couldn't tell me the necessary parameters to set up the EIP communications with a Unistream. They could only direct me to an EDS file online. With past experience, the EDS file print out, and some trial and error I found the following parameters to work: Input Assembly Instance: 100, size 24 Output Assembly instance: 150, size 10 Configuration Assembly Instance : 5, size 0 Check the box for "Use Run Idle for O2T" on the Output Assembly Instance For the Creators: Is there any plan to eventually be able to install EDS files through Unilogic? This would greatly speed up the development time. Quote Link to comment Share on other sites More sharing options...