Patrick M Posted July 12, 2011 Report Share Posted July 12, 2011 I see where the V280 controller has an operational temperature range of 32F - 122F. My question is as follows: 1. Does this temperature range reflect the ambient internal temperature of the panel box it's installed in? Or, 2. Does this temperature reflect the internal temperature sensor displayed on SI 14? The example below is a real word issue we are seeing: We have a V280 installed in a 24" H x 16" W x 10" D panel box. The ambient external temperature of the box is 80 degrees F. The internal ambient temperature inside the box is 93 degrees F. And SI 14 lists the temperature as 118 degrees F. Which of those three temperatures is the one we should be concerned with when it comes to the operating temperature range of 32F - 122F? Please let me know if I can provide more information. Thank you in advance for your help. Pat. Link to comment Share on other sites More sharing options...
Emil Posted July 13, 2011 Report Share Posted July 13, 2011 Hi Pat, The "real" one is those shown by SI14. With good ventilation, it needs ot be few degrees above the ambient. In a small, closed plastic box because of heat, emmited by the controloler itself, ti can be much higher than the ambient. Link to comment Share on other sites More sharing options...
Patrick M Posted July 13, 2011 Author Report Share Posted July 13, 2011 Thank you for your quick response, I'll be sure to pass this along to our design engineers. Link to comment Share on other sites More sharing options...
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now