DannyC Posted July 15, 2011 Report Posted July 15, 2011 Hi, We have a M91-2-T1 that we haven't used for a while, and have just got it out again recently. I am trying to communicate with the PLC via RS232, but cannot communicate with the PLC. I am using: USB to serial cable (Prolific, driver version 3.3.10.140), connected to; DB9-RJ11 cable which we made according to the pin assignments in the U90 software manual (we also have another one with the RxD/TxD reversed because we thought we had the two around the wrong way) I also tried using an older computer which has a RS232 port, and no luck there either, so that ruled out the problem of the USB to serial cable. I have checked the COM port and settings (reset everything back to default), and they all seem fine. Is there a way I can test if the connections are correct by say, use HyperTerminal to send commands to the PLC, or is there any way I can find out what the problem might be? Many thanks, Danny
AlexUT Posted December 13, 2011 Report Posted December 13, 2011 Hi Danny, I am sorry for missing your request for help. Was the problem solved or you need further help? * PLC can not answer to any HyperTerminal input as by default it use VisiLogic communication protocol. ** To check cable or adapter, you need to shortcut pins 2 and 3 at 9 pin RS-232 connector. Entering any symbols from HyperTerminal will echo back.