roghenr Posted January 3, 2022 Report Share Posted January 3, 2022 I need to take a thermocouple reading between 0 and 1000 degrees Celsius. I'm using inputs 5 and 6 with type k. I want to see this temperature value at ihm, but it seems that my linearization is not ok. I'm simulating values but the reading remains at 35.9 degrees. What am I doing wrong? Link to comment Share on other sites More sharing options...
roghenr Posted January 3, 2022 Author Report Share Posted January 3, 2022 Link to comment Share on other sites More sharing options...
MVP 2023 Flex727 Posted January 3, 2022 MVP 2023 Report Share Posted January 3, 2022 Thermocouple readings are in degrees as read from the I/O module. No linearization is necessary. The value read directly from the module will be degrees x 10 since the measurement is to the tenth of a degree. Link to comment Share on other sites More sharing options...