sts098 Posted September 28, 2023 Report Posted September 28, 2023 It appears that I MUST hard code the client IP in order to use the native Modbus Functions. Otherwise, I am forced to use UDF's to access my Clients, and poll these through ladder to get values. Is this correct? Many times, the IP is unavailable, or Multiple identical controllers running the same program are supplied to customers. Currently, each program must be individually modified and uploaded to the HMI/PLC. Each of these HMI/PLC must be identified so installation occurs at the given machine. Much easier to simply changing a stored IP address for the slave. I would much prefer to use native Modbus functions. Will this be addressed? Is there a technical reason you do not allow the ModBus Client IP to be configured via ladder and HMI?
Gabriel Franco Posted September 28, 2023 Report Posted September 28, 2023 In the Modbus IP Configuration FB, you can assign the IP address of the slaves to MI registers and then assign them from HMI If you are talking about Unistream Series (as I suspect you do), it is possible to modify the IP of the slaves from Uniapps rather than change program and download it to the PLC.