  1. What Emil says is of course true. However, if you are stuck with the M91 there are a couple of other things that may help.

    1. Whilst you can't poll modbus and connect U90 ladder in debug mode at the same time, you can include the logic in your program that allows you to manually suspend the Modbus polling so you can connect U90 Ladder. If you re-trigger the modbus initialisation with a ---|P|--- coil (placed in parallel with the power-up bit), then you can re-start the Modbus comms without needing to cycle power.

    2. to debug the modbus comms you can use a PC-based modbus program to listen on the RS485 network. At the basic level you can see the Hex data from the PLC and the slave, but you might be able to find more advanced software that can do some decoding of the Modbus packet.

  2. The RTC to ASCII has a format for dd/mm/yy, but you need to scroll down to the bottom of the list to see it. See screenshot below:

    post-16-005459700 1313710273_thumb.jpg

    If you need the format dd-mm-yy instead of dd/mm/yy then some further manipulation will be required.

    I haven't done much with them myself, but the Strings functions seem to provide just about every option you need to achieve this without too much programming.

  3. What program have you started with to write the Jazz Modbus program? The standard U90 Ladder example is written for the M91 and won;t work on a jazz with the MJ20-RS4 (JZ-RS4) comms adaptor. You need an additional Com port ocnfiguration step.

    Please see screen shot below for the critical step, added after the Modbus config rung. I have also attached the sample project files. I think these file was originally sent to me by Unitronics support, but IMHO they should be in the U90 Ladder examples.

    post-16-061044200 1313107296_thumb.jpg

    Modbus Slave Jazz RS485.U90

    Modbus Master Jazz RS485.U90

  4. I would say most forum users (myself included) would not know what a Delta Robot was. Here is a link:

    http://www.sigmatek-automation.us/pdf/eng_delta-robot.pdf

    If you are planning to drive the actuators directly, polar coordintate calculations would be required for the kinematics. There are no built-in kinematic functions in the Unitornics PLCs, but they do have a limited amount of floating point variables and a full set of trigonometric functions.

    Depending on your machine setup you may be able to store all the desired trajectories as lookup tables rather than generate them on the fly. This would allow you to calcuate the trajectories offline on a PC and just transfer the final data to the PLC data tables.

    Either way this would not be a simple project.

  5. But if the PLC has put itself into stop mode how can it then set SB24 or SB300?

    I think the original question was asking can this be done without user intervention. Kind of like a self-resetting watchdog - if the PLC goes into stop mode, automatically reset it.

    Possibly you would want a limit on the number of times it would self-reset, so if the fault was permanent the PLC would stay in stop mode after a certain number of reset cycles.

    Note also that if the PLC is being remotely monitored, SB302 will indicate if the PLC has gone into stop mode, giving the possibility to reset the PLC via remote connection.

  6. It is possible to set up the PLC GPRS connection in listen mode, but I haven't done it. However you now have the same problem turned around the opposite way. Once the PLC has registered on the GPRS network you need to know it's IP address. So have it send you it's IP address via SMS before putting itself into GPRS listen mode. You probably need a GPRS_RUN FB in there somwhere as well.

    Another gotcha is that the cellular provider may block incoming requests to the GPRS device, particularly if they come from outside the cellular network. If it doesn't work from an ADSL (or similar) cable-based internet connection, try connecting with another GPRS modem using the same cellular provider as the remote PLC modem. Remeber that the main commercial use for GPRS is internet browsing on mobile phones - so teenagers can do important things like get on facebook and download ringtones.

  7. Flavien:

    Well, I never had any problem to send SMS at this baudrate with enfora modems, but I never tried to establish a connection at this rate.

    SMS will work fine at the higher baud rate since it just involves comms between the PLC and the modem (then the modem "does its own thing" as far as sending the SMS onto the GSM network). It's just the dial-up connection that seems to work best at 9600 since the "over the air" data rate is limited to 9600, and there is an end-to-end connection involved.

    TT-ZX:

    If you use GPRS you can use SMS on the same modem. There is a good example for GPRS in the Visilogic help files. Basically you use SMS as the primary method of communication with the PLC. When you want to set up a GPRS conneciton, send the PLC an SMS to initiate the GPRS connection from the PLC end. When you are finished with the GPRS connection, either terminatie it in the PLC from the remote connection or have a timout on the PLC that drops the GPRS once there is no host connected or no data for a certain period of time. The limitation is that you can't send or receive an SMS with the GPRS connection active.

    For this to work you also need to set up port forwarding in your PC internet connection, and know what the current public IP address of your PC broadbnad modem is (or pay for a static IP address on your PC connection).

    If you go the route of using an Ethernet broadband modem, then SMS is usually not an option. We have a customer who has tried in vain to find an ethernet modem that also has a serial port that allows SMS. One possible option is to use email instead of SMS.

  8. Not sure how it works elsewere, but in Australia the network sets the baud rate for dial-in (CSD) GSM connections at 9600baud. Since GSM base stations are only made by a few manufactuers, I presume this is going to be reasonably consistent across the globe.

    I have tried setting the modems to 57600, but it does crash out. I presume the 9600baud GSM link causes timeout and/or buffer problkems with the 57600baud local serial links

    For high data rate the other options are to use a Packet Switched Connection (like GPRS) or use a stand-alone broadband modem with Ethernet (and fit ethernet to the PLC).

  9. Hello Jason,

    Go to the Tech Library section of the Unitronics website

    http://www.unitronic...chnical_Library

    there are specification documents for each model, and usually in the section on analogue inputs there will be a conversion time.

    The final sample rate is a function of the conversion time and PLC scan time. If the conversion time is longer than the PLC scan, then it will determine the sample rate. Otherwise the PLC scan time will determine the sample rate.

  10. HI Cara,

    It looks like your response is steering in the direction of zooming out rather than zooming in. In the case I was dealing with, the customer didn't want to zoom out so he can see all the screen. He wants to be able to zoom in on a smaller area so he can see in more detail. So it would probably require a combination of zoom and scroll, or the ability to select a window of the display and zoom in to it.

  11. At present the only thing I am aware of that comes close to this is the ability in the Remote Access utility to read/write the entire memory of the PLC to/from a spreadsheet.

    So you could create a spreadsheet from a new (or freshly initialised) PLC, with blank values, then enter your one-time initialisation values. After download of the project you then update the operands in one step using this spreadsheet. I know it is a bit of double handling, but it is less steps than setting each value individually, and also provides more certainty that you won't miss something.

    I would like to see this built-in to Visilogic, both as a programmer's tool to set initial values, but also as a service tool, so on project upload the live values are also copied. The latter would allow very simple replacement of an operating PLC in the field.

  12. I doubt the cable is a problem over such a short distance (though some may disagree). I have had CAN working over several different "non ideal" cables, though usually just for testing. However I would always recommend using the specified cable type for a permanent installation.

    Also, if the communications is working in one direction, that would indicate that the cable is transmitting the data OK.

    Check things like your unit IDs and CAN status bits and integers.

    What is triggering the send that fails to be received? If you are trying to send too fast there will be problems. If it is event-driven, check whether you have a vibrating/bouncing contact or fluctuating analogue signal that is triggering a send more frequently than you expected.

  13. It sounds like you need to create an image cache file. This can either be created from Visilogic or from the PLC.

    If you create from Visilogic, save the file to disk then import it into Remote Operator.

    If you create it directly in Remote Operator, it retireves the images back from the PLC and creates the file itself. This can be slow if you have a slow connection and/or lots of kB (or MB) of images.

    Hope that helps.

  14. From one of Ofir's posts in the old forum:

    if you want to disable the Info key in jazz you can set SI 178 to zero.(default is 3)

    When using M91/Jazz controllers you can set Info password on the System menu only and this password related to SI179.

    Note that when you enter new password to SI179 you will not able to see it via the U90ladder and the value of SI179 will allways shows 0.

    These operands are not tagged in U90 Ladder with any description.

  15. Hi Nacho,

    I have been requested for BACNet comms a couple of times also. My initial impression was that the physical layer of the communications would be the main problem. However if BACNet can operate on RS485 then that obstacle is removed. The next question would be to make sure the target devices are using RS485 compared to the other types of physical layer available. Once the question of Physical layer is resolved, the next issue is implemention of the protocol.

    As per Keith's post above, I don't see an easy off-the-shelf way of doing this directly out of Unitronics. If you can obtain a BACNet slave to test with, maybe you can get a limited number of messages working.

    Unitronics protocol is generally quite flexible. A couple of areas have caused me concern:

    * use of the NULL (0x00) character as a string terminator. If you are trying to implement a binary ASCII protocol that can contain NULL characters inside the string, the Unitroncis PLC will stop transmitting (or receiveing) once it sees the NULL. This can result in only part of the string being transmitted or received.

    * DLE-doubling and other escape sequences. The 3964-R serial protocol uses the character 0x10 as an escape character. If it appears in the middle of a string it must be repeated to ensure it is not interpereted as an escape sequence. There is no built-in way that I can see to implement this type of feature in the Unitronics Protocol blocks. I think it could be done in ladder, but would not be pretty.

    I haven't gone over the BAC protocol to see if either of the above issues arise, but that is a summary of my experience so far.

×
×