Do not use a regular coil more than once in your program. I think you could change the MB 143 instances to Set Coils and it would work (according to the Help file the OS Resets the coil when it refreshes the screen).
- 1
-
Sounds like the HMI string element is not being updated with the latest data. Make sure the MB you have in the "Link" field is being triggered when you want to refresh the screen.
-
Moved to VisiLogic forum.
-
1 hour ago, Ausman said:
In chasing a particular component, I stumbled onto this site and noticed it's humour page. Good for a bedtime read.....
Funny stuff!
-
I rarely work with the V230, but my recollection is that upload project is enabled by default on these PLCs. You can choose any of the 3 download selections, as appropriate.
-
I'm always looking for this and decided it should be Pinned.
-
15 hours ago, kvlada said:
Reason is that VisiLogic doesn't allow you to download a ladder application if the PLC OS is not the same as one in VisiLogic. What happens when I have to make some changes to an app which was made with an older version of VL?
Of course, I could have many virtual machines with different VisiLogic / UniLogic versions, or use Version Swapper, but these are just complicated band-aids.
Nothing complicated about it. UniLogic allows as many different versions installed simultaneously as you wish. Just select the correct shortcut when starting up the software. VisiLogic has one extra step (running Version Swapper), but still you don't need anything like separate "virtual machines".
-
23 hours ago, kvlada said:
I've always updated Unitronics PLCs to newest firmware (both U90, Vision and UniStream) as soon as it's released.
Personally, I believe this to be a huge mistake. PLCs are not like Windows computers & software. Sometimes there is a specific reason for upgrading (important and needed new feature being added, internet security, bug causing your particular installation problems being fixed, etc), but routine upgrading just because a new version is out - no.
-
DanT has provided some excellent help. I will add that you need to get some of the terminology correct so that your searches will be more accurate:
UniStream - the PLC hardware (PLC+HMI device), there are various models of the UniStream PLCs
UniLogic - the programming software for the UniStream hardware
Unitronics - the manufacturer of the hardware and programming software
7 hours ago, Chris Edwards said:Sadly, I don't a have UniLogics controller to play with so I'm resorting having to go through YouTube and other online material and it's a serious mountain to climb
I strongly recommend that you purchase the hardware you will be programming as soon as you possibly can. There are no logic simulators and your project development will require that you experiment and test as you go along.
- 1
-
Have you tried removing and replacing with the same CPU, not just rebooting? Is the PLC subject to a lot of vibration?
-
-
This looks to me like a single device and you choose which scale reading via MODBUS command. I see no reason to close the connection, once established, nor any reason to use two sockets.
I'm not familiar with these scales so I may be misinterpreting something. You can choose the timing between commands without closing the socket.
-
This makes no sense to me. If you were communicating as though it was one device, then why was it necessary to close the connection between MODBUS commands?
-
35 minutes ago, Jhav said:
they share the same IP address
That's your problem - you can't have two devices on the same network with the same IP address.
-
It's telling you what the problem is: "Stop reason ; No Application"
This means exactly what it says, there is no application in the PLC. This can be caused by several things, but most likely due to removing power from the PLC with no battery or a dead battery. The solution is to replace the battery and reload the application from VisiLogic.
-
Why are you trying to communicate with two different devices through the same socket? Use two different sockets, one for each scale - then you don't have to waste time connecting and disconnecting.
-
I think you should use v.9.8.96 for database 155.
-
8 minutes ago, ScottF said:
Is there a "database table" to Visilogic version cross reference available?
This pinned post is where we've been collecting that information.
8 minutes ago, ScottF said:It would sure be nice if the information / error dialogs could be copied to the clip board.
Try Alt-PrtScrn.
-
14 hours ago, kratmel said:
old joke....
And one of the few that doesn't work when spoken aloud.
-
Have you elevated this to Unitronics Support (support@unitronics.com)? Keep in mind that this is a user forum staffed by volunteer users who for the most part are not Unitronics employees. Most of the people here do not have the type of specialized knowledge you are seeking. In any case, I recommend patience as most forum members likely don't check this board every day.
-
16 minutes ago, Easy Pete said:
Is there any progress regarding this or some sort of workaround?
@Cara Bereck Levy do you by any chance have an update for us?
-
You can request it from support@unitronics.com
-
Did you install the driver?
-
If instead you are asking if there is some way to download images without VisiLogic, the answer is no.
- 1
Programmable timer
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
By "value", do you mean the Preset time? If so, use the function "Store Timer/Counter Preset, under the Store menu.