Posts posted by bbcxo
-
-
-
Heating Element: DERNORD Immersion Cartridge Heater 120V 1500W Hot Rod Heating Element Replacement 3/4 Inch Thread
Pressure Sensor: Psi Pressure Transducer 4-20mA Output G1/4" Silicon Pressure Transmitter Transducer for Water Gas Oil (0-0.2MPA)
- using 0-30 psi
Relay: Inkbird Solid State Relay 40DA DC SSR Black Heat Sink for PID Thermostat Temperature Controller
-
Load Voltage: 24-380VAC
-
Load Current: 40A
-
Input Voltage: DC 3-32V
Power Supply: 120-24
Temp sensor rtd pt100
Aim for the the program is to control the air pressure in an enclosed tank via a heating element. I'm assuming due to getting an error with the PID status instruction being false, the PID/Auto tune/PWM/heating element won't activate/start. Other than that, pretty lost on why the system isn't functioning. We've checked that all sensors are working.
-
@Joe Tauser I attempted to make the changes you suggested. Sorry If it still needs more work new to PLC/Unitronics/Visilogic. Please let me know if there's anything I need to fix
-
Thanks for the feedback. I will make some changes and reach back out. Do you think I should get rid of the temperature loop all together?
-
Focusing on pressure. Not using any fluids/steam. Just the enclosed air in the tank. Heating element 300w. Don't want to go higher than 15 psi in the tank
-
Hello,
Wanted to get feedback on the project I'm working on. I've attached what I have so far. SD portion still under construction
Overview:
Controlling pressure with a heating element inside a tank utilizing PIDs
Specs:
PLC: V700
Snap on: V200-E3/4XB
AI:
Pressure Sensor: 0-145 psi/ 4-20ma
Temp Sensor PT100: -50-300 C
Question:
How should I implement the selector switch logic/code to choose between the pressure/temperature loop?
Feedback:
Auto tune parameters
Linearization Block
Overall Check of Program would be appreciated
-
@kratmel No logic is needed to display the temperature reading on the HMI?
-
Hello,
I was seeing if someone could post logic/code on how to get the temperature reading from the sensor and then how to display the reading onto the HMI.
Also, how to wire the sensor on the plc
PT100: https://www.amazon.com/Pt100-Temperature-Sensor-Probe-Thread/dp/B074NVDCC4
PLC: v700
Snap on: V200-18-E3xb
Thanks!
-
Hello, New to using PLCs.
PLC: V700, V200-18-E3/4xb
https://www.amazon.com/dp/B0748BHLQL?ref_=cm_sw_r_cp_ud_dp_MPKEBK3VM6AV7174NC1Q
Pressure Transducer: 0-100psi
Output: 0.5V~4.5V linear voltage output. 0 psi outputs 0.5V, 50 psi outputs 2.5V, 100 psi outputs 4.5V.
I wanted to know how would I setup the pressure transducer in the Hardware configuration....Analog Inputs...type...mode, as well as what settings to use for the linearization block.
Error with Pressure Loop PID Heating Element
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
Thanks. Got it up and running