In my project on the V120-22 I use 2 COM ports for RS485 Modbus communication. Port

2 - Master mode to communicate with another device, the Port 1 - Slave mode for

communication with the upper level.

After some time, the PLC stops responding via Port 1, while Port 2 is operating

normally and ladder is operating normally too. Helps only restart the PLC. If Port 2

is disabled, then the connection through Port 1 is without failing.

It seems, as if at the time of simultaneous access to the ports, there is a conflict.

Why lost communication with Port 1?

Ports settings:

Port 2: 115200, 8, none, 2

Port 1: 57600, 8, none, 1

The request to Port 1 is sent after a pause of 10 ms after the last response

Connection breaks after 2000-15000 requests

Best regards,

Anton

Link to comment
Share on other sites

Upload your program.

Joe T.

Thanks for your response.

Sorry, I can't upload the program, because I'm not the author. And the program is awkward, this can be a cause of the error. I solved the problem as follows: set the check bit SB135 (COM Port 1, Data Receive) before sending the requests to Port 2 and reduced the baud rate to 9600.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...