Thermocouple reading V350-35-TA24
AAA86
Hi,
I have a problem.
I have 2 same main boards of the PLC V350-35-TA24 with same HW and SW configuration, but there is a problem. 1 of the PLC is reading the Thermocouple temperature and the other reading constantly -0.1C.
I've passed the configuration a lot of times, the boards REVs and etc. it all the same....
there is probably something in the way tha confusing the Thermocouple reading in the main board but i can't find it. Is anyone can help me by providing me a solution or schematics or where the thermocouple is connected to the main board and rhough what devices it going.
Thanks in advance.
  • 2 weeks later...
Hi,
0.1C difference between 2 OPLCs is not a problem.
From Datasheet:
Resolution is 0.1 C.
Cold junction compensation error ±1.5°C maximum.
Full-scale error ±0.4%
Linearity error ±0.04%
Warm-up time ½ hour typically, ±1°C repeatability
Everything is in range.
So why do you panic and require schematics?
It seems useless. Isn't it?
My advice is to use it as-is. I see no problem in your configuration.
BR
  • MVP 2014
It sounds like one of your thermocouples always reads -0.1C regardless of temperature.
As Alex suggests, the scehamtic is not going to tell you much.
I would check:
* swap thermocouples to ensure they are both working
* ensure the thermocouple is connected with the correct polarity
* configure another thermocouple input on the same PLC.
The most likely problem is a faulty probe, incorrect/faulty wiring or configuration error. If those can be conclusively eliminated, then perhaps there is a faulty input on the PLC, but that is the least likely, based on my experience.