hi all,

i have a question about using protocol fb. i have a phoenix empro ma250 power meter which can aommunicate using modbus rtu. i can communicate with the power meter using read holding register modbus fb flawlessly. what i want to do is use protocol fb to generate the send and receive modbus frame messages. i am having trouble constructing the messages in protocol fb. i have attached a picture of the frame structure of the meter. iam using a v350 for this, with one port for modem and the other port for the device/s. i wish to use protocol fb instead of modbus fb because i want to connect other devices that don't use modbus protocol. i hope anyone can help me.

thanks all

protocol fb question.bmp

  • Upvote 1
Link to comment
Share on other sites

Hi pgold,

That’s my problem too, I’ve wanted to communicate phoenix power meter EMPRO MA250 with FB Protocol, but it seems I am having a problem in construction of framing message or parameter configuration of such function block. However I’ve posted some screen, I made an application were I should be able to read power meter single register such as phase voltage.

post-292-0-89557200-1366769065_thumb.jpg

post-292-0-46987400-1366769084_thumb.jpg

post-292-0-96047000-1366769097_thumb.jpg

Thanks

Link to comment
Share on other sites

hi emil,

i considered the conflict of the two protocols that is why i want to use fb protocol and not modbus. if i use fb protocol, then i can initialize the com port for protocol fb. i can communicate with the first device via fb protocol but i don't know how to construct the messages in the attached picture for the second device which is the power meter

Link to comment
Share on other sites

Hi Paul Have seen your FaceBook message and have read the gist of your requirement. I think the answer is Yes, it can be done, the Modbus frame is small and can be constructed using the Protocol FB. I am training all day Thursday but if you would like to talk through your problem on Friday my number is 01480 276446.RegardsTony. Tony Spearing - Technical Manager, i4 Automation Ltd

Link to comment
Share on other sites

Hi Paul

As you had also put through your question on Facebook I assumed you were UK based.

I used the coms sniffer on a V570 to look at a known working Modbus command, read holding registers 0-31 and then tried to duplicate the message using the Protocol FB. I came across a small snag in that the CRC byte order in wrong, it's back to front.

The working message is

01 03 00 00 00 20 44 12

which the Protocol FB generates as

01 03 00 00 00 20 12 44

I cannot see a way to reverse the CRC bytes automatically but as I guess you do not need to have many messages you could work out the CRC using the above method and then hard code it in the Protocol FB. The method for generating the CRC for Modbus appears to be binary, zero forward offset, zero backward offset, CRC-16, 256 (100H), 2 bytes.

Note that the message is only 8 bytes long including the CRC, the screen shots added by Nouy would look like this for my message, two extra bytes at the front of the message.

00 01 00 03 00 00 00 20 xx yy

Hope this helps but if you still have issues them please get back to me.

Tony

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...