mckruger Posted February 19, 2014 Report Share Posted February 19, 2014 Hi I have a pressure sensor that i use on a V570 and V200-E1B snap-on. The sensor is 4-20ma sensor. I've set the analog input to 0-20ma. On the E1B each analog input has the following: V - Positive I - Input Signal (Positive) 0V - Negative It work fine on the E1B Now im trying to use the same sensor on the V200-18-E46B Which has the following analog Inputs AN0 AN1 AN2ACM - Negative Ground AN3 - High Pressure Sensor (Positive) AN4 AN5AN6 - 8 But it gives me a value of 1024 on the system. which according to the booklet mean "Deviates above the input range" Has anyone got a solution ? Quote Link to comment Share on other sites More sharing options...
transpondster Posted February 21, 2014 Report Share Posted February 21, 2014 have you changed jumpers, defaults most likely 0-10V Quote Link to comment Share on other sites More sharing options...
mckruger Posted February 21, 2014 Author Report Share Posted February 21, 2014 There was a jumper inside the V200-18-E46B that changes the type of the analog input from voltage to current. Sorted out the issue,. Quote Link to comment Share on other sites More sharing options...