Gabriel Franco Posted May 23, 2014 Report Share Posted May 23, 2014 To wire several EX-RC1 and a Vision controller, it should be a "daisy chain" or may I use a star topology?. In last case, which modules should be terminated? Quote Link to comment Share on other sites More sharing options...
dan Posted May 23, 2014 Report Share Posted May 23, 2014 Hi Gabriel, A daisy chain topology is the correct way to wire a canbus network. Termination occurs at both ends of the line: TPLC- Terminated PLC (Or EX-RC1) PLC- Non terminated PLC (or EX-RC1) TPLC----PLC-----PLC----PLC----TPLC Quote Link to comment Share on other sites More sharing options...