darknesspic Posted August 15, 2015 Report Share Posted August 15, 2015 Hi all, I'm using v280 and my PID input is 4-20mA (-60-60c),setpoint is degree c, output is 0-5v. Please advise the limit cv,pv what should they are? Thank you. Link to comment Share on other sites More sharing options...
Gabriel Franco Posted August 15, 2015 Report Share Posted August 15, 2015 PV low limit: -60 PV high limit: +60 CV low limit: 0 CV high limit: 10000 (Equivalent to 100.00% with 2 decimal places), then you must linearize CV to your analog output to 0 ... 5 V, using X1 = 0, X2 = 10000, X = CV. Y1 and Y2 values depend of your analog output card. Link to comment Share on other sites More sharing options...
Walkerok Posted August 15, 2015 Report Share Posted August 15, 2015 Knowing that you have a 4-20ma temp sensor that you have to scale to show -60 to 60 on a screen. After you linearize the temperature everything can be compared to the final degrees celcius engineering units you are using so your min and max limits should be -600 to 600 (I am assuming you will have 1 decimal place. Good Luck Keith Link to comment Share on other sites More sharing options...