Hi All

So I'm doing a new project involving a V560 (looks good!) and 3 x SEW motor drives. The drives can be controlled by either Modbus RTU or analog control signals. In previous projects I have used the analog route for simplicity/robustness. Modbus offers some improved functionality.

Having spent a large amount of time looking at Modbus in the Visilogic help files, help from other forum members and the drive documentation, I am still leaning towards analog.

A basic Modbus implementation would involve 4 read/write parameters (registers 1-4) and 7 status reads (registers 5-11) (For each drive)

Example:

Request:

[01] Drive address[03] Command [00][05] Register start address [00][01] No. of registers [94][0B] Checksum

Reply:

[01] Drive address[03] Command [02]No. of data bytes[00][00] Data[b8][44] Checksum.

Is there a checksum function or must each string be pre conceived?

Looking at the examples I see plenty of unitronics - unitronics master/slave applications. How different is Unitronics - (Other Vendor)? Examples would be good.

Is it practical to suggest a standard format datatable and ladder structure so users can share datatables of various devices? This is sort of bordering on UDFB, but I didn't want to say that out loud!

Sorry- as you might tell I'm a bit of Newbie in this dept.

Thanks.

Link to comment
Share on other sites

  • MVP 2023

If you use the Modbus function blocks you won't have to worry about formatting the data packets or checksum as you describe. The block does that for you. There are Modbus examples that are a good starting point.

You will have to do your own handling of the commands to each drive, writing a program that will trigger read and write blocks individually and not crashing into other blocks while they're busy. Start by connecting one drive and getting a feel for how the Read and Write blocks work, and then adding the other drives and sequencing between blocks for those.

Don't forget that Unitronics is 0 based and Modbus is 1 based. If you're not getting the right data, try subtracting 1 from your start address.

Post your code as you go along if you run into problems.

Joe T.

Link to comment
Share on other sites

If you use the Modbus function blocks you won't have to worry about formatting the data packets or checksum as you describe. The block does that for you. There are Modbus examples that are a good starting point.

You will have to do your own handling of the commands to each drive, writing a program that will trigger read and write blocks individually and not crashing into other blocks while they're busy. Start by connecting one drive and getting a feel for how the Read and Write blocks work, and then adding the other drives and sequencing between blocks for those.

Don't forget that Unitronics is 0 based and Modbus is 1 based. If you're not getting the right data, try subtracting 1 from your start address.

Post your code as you go along if you run into problems.

Joe T.

Thanks Joe

That clears up a few things, will give it a go!

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...