Good day. I´m new at using PLC so i reach to you for some guidance.
I have a PLC v570 and i need to register a table when the bobine is turned on or off, in other words, registering 0/1 (or off/on). I´ve registered other information in the table before without any trouble but with the bobine´s registry i found myself a little lost. I'd really appreciate your help. Greetings.
 
Link to comment
Share on other sites

Hi,

If you wish to log to a data table a value of 0 or 1 you can define the specific column to Boolean and store a value of MB.

If you are still facing issues with logging values to the data table , attach the application and explain where is the logic that stores the data to the table.