boris david diaz guerra Posted September 14, 2017 Report Share Posted September 14, 2017 Hi good day I have a problem with a PLC V280 with the adjustment module V200-18-E3XB. this is the case -I have configured the TC module inputs, with jumpers 3-4-5 for AN0 on B. -HW configuration is for TC J, without filter, ° F, MI 104 -I have a type J TC connected to the analog input AN0, which reads in another PLC and indicates well -program a screen with a Variable: numeric, to display the MI 104 The problem is that the display shows the value 32767 and I do not see the actual value of the temperature. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted September 14, 2017 MVP 2022 Report Share Posted September 14, 2017 Hi Boris, 2 things come to mind initially, which need to be known before further discussion. 1). The E3/4XB won't work properly unless it is correctly powered. You have done the jumper placements, so you must have the pdf/manual that also has the power connection requirements. It is very easy to miss some of the connections as they are in different areas of the manual, depending on what they power. Physically look at your wiring of the module terminals, if you see anything with a "V" without a connection, this needs to be learnt and corrections made. 2). Do an initialise and reset via Connection/Communication & OS/2nd Tab/bottom right after finishing everything. cheers, Aus Quote Link to comment Share on other sites More sharing options...
boris david diaz guerra Posted September 15, 2017 Author Report Share Posted September 15, 2017 Thank you very much. I Will review the connections and communicate again. Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.