plcfox Posted March 2, 2018 Report Posted March 2, 2018 Hi All having trouble configuring V700 with V200-18-E3/4XB snap in to a 10 v pressure transducer have set up linear values 14 bit have input set up correctly have internal jumpers set to voltage AAA etc still cannot get change in value just need some help had trouble finding data on V200-18-E3/4XB so not sure if i am setting jumpers correctly PLCFOX.
MVP 2023 Joe Tauser Posted March 2, 2018 MVP 2023 Report Posted March 2, 2018 Make sure you have +24V power connected to the V2 power connection. The -E3XB requires power in more than one location. Joe T.