Hi,

I am new to Unitronics and VisiLogic. I am trying to connect a motorized valve to my Unitronics v130. I know that with the valve, I need to use the analog outputs. However, I am not sure how the ladder diagram should look like. All I want it to do is open and close a motorized valve. I was planning on using F1 and F2 as the on/off switch respectively. I am using a W.E Anderson Motorized Valve ZV20224.

Can someone help?

Sorry for my ignorance.

Link to comment
Share on other sites

  • MVP 2022

First of all, are you certain the valve is controlled by an analog signal rather than a digital signal? If so, is it 0-10V, 0-20mA, or 4-20mA? Set your PLC jumpers accordingly. You can get the information you need on this from the Unitronics website (unitronicsplc.com).

In the software, you will need to go to the Hardware configuration and configure your analog output per the above and assign a Memory Integer (MI) to the output. The V130 has 12-bit resolution, so that means you need to store a value between 0 & 4095 (819 & 4095 for 4-20mA) in the MI you've assigned. 0 (or 819) will be fully closed and 4095 will be fully open.

In your ladder you will have a positive transition of the System Bit for F1 (SB 58) store 4095 to the MI and a positive transition for F2 (SB 59) store zero (or Reset Numeric) to the MI.

Easier than pie. :)

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...