good afternoon , we have a question about the following fuctionality Toggle coil ,  if we have  contact with positive transition rise   P ( from Key 2 from  front panel ) as you know when we push it we select the key 2 button from controller 120 R22  it would generate a pulse , at the first time when we do that , the toggle coil (x) result would be 1  and this value would be kept  until ,the second time  when we push  agan the keypad 2  then  the toggle result (x) would be 0  , Is it correct ?  

Please see the attachment here we show the configuration 

TOGGLE LOGIC.gif

Link to comment
Share on other sites

  • MVP 2023

Not quite.  You've reference TD 0 but not activated it using a coil assigned to the timer's address.   Also the Toggle coil will toggle on and off every other scan because you're continuously triggering it.  Always use a P contact with a keypad bit and with toggle coils.

You don't need MB 0.

I think this is what you're looking for-

image.png.a93a78883a1686df261be652a960639e.png

The timer will reset itself when you remove power (net 2).

Note that if you press Key #2 again while the bit is ON and the timer is running then you will toggle the bit off.  If you want it to stay on, replace the toggle coil in net 1 with a SET coil.

Joe T.

 

  • Like 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.