MartinIT Posted March 5, 2019 Report Share Posted March 5, 2019 Hello, My HW configuretion: V1040, UMI-0004BE-B1., SW 9.8.79., MODBUS RTU communication setting 19200,8,E,1. Whem motor is running I have in Status messages=10 - Incorrect CRC (in picture MI2322) Where is problem? What can I do to be Status messages =0 ? Thanks Martin Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted March 5, 2019 MVP 2022 Report Share Posted March 5, 2019 What with communication cable shielding? Connected according to the manual? Is it shielded cable used for motor connection? Is it VFD and shielded motor cable correctly grounded? Is it communication OK when VFD is stopped? Quote Link to comment Share on other sites More sharing options...
MartinIT Posted May 6, 2019 Author Report Share Posted May 6, 2019 (edited) 1. Communication cale has a shield. Conection according the manual. 2.Motor has a shield. 3.VFD has corecly gounded. 4. Comunication OK when VFD stoped. MI2322=0. When hte motor is running - MI2322 has 4,5,10( MI2322 = 4,5,10, 4- Master-Time Out,5-No Comunication,10-Incorect CRC) 1.Can be wrong the VFD parameters setting? My parameters: VFD- P14.00-1,P14.01- 4, P14.02-1,P14.03-100,P14.04-0.0s,P14.05-0 2.Can be wrong the config parameters ? My config is: Com2,19200,0.5,8,E,1,RS485 Martin Edited May 6, 2019 by MartinIT Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted May 6, 2019 MVP 2022 Report Share Posted May 6, 2019 If communication OK when VFD is stopped - your parameters and configs is OK. Is it terminator (120 Ohm resistor) present on both side of the line? Please also see this topic Quote Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.