safchow Posted April 17, 2019 Report Posted April 17, 2019 Hello, I am a first time user for the program and so far i've been learning from using the tutorials and i'm struggling to configure a relay output connected to a solenoid. So from what i've found i believe i have assigned the solenoid to O0 and have added this to my ladder. Can anyone confirm if this is correct? essentially i need the solenoid to open when a button is pressed for 2 seconds. Thanks in advance
MVP 2023 Flex727 Posted April 17, 2019 MVP 2023 Report Posted April 17, 2019 2 hours ago, safchow said: i need the solenoid to open when a button is pressed for 2 seconds This is ambiguous. Do you want the output to turn on for 2 seconds after the button is pressed (this is what you have), or do you want the output to turn on after the button has been held down for 2 seconds? Also, you appear to have the Power-Up for O0 as SET. This will turn on the output as soon as the PLC boots up. Is this what you intended?
safchow Posted April 17, 2019 Author Report Posted April 17, 2019 I would like the output to be on for 2 seconds. and no I need the output to only be active when the button has been pressed
MVP 2023 Flex727 Posted April 17, 2019 MVP 2023 Report Posted April 17, 2019 15 minutes ago, safchow said: I would like the output to be on for 2 seconds. Then what you have will work except that the output will already be on due to the Power-Up setting. Change that setting to either RESET or NONE.
MVP 2023 Flex727 Posted April 18, 2019 MVP 2023 Report Posted April 18, 2019 5 hours ago, safchow said: Thanks for the help! You're welcome. I do have to make a correction. Due to the fact that your ladder has a direct coil for O0, the Power-Up setting will have no effect. Turn it off anyway.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now