pesi78 Posted June 15, 2019 Report Share Posted June 15, 2019 Hello, I have an issue I have made a new ladder routine "NO LIMITS" with soubrutine "TEST 1" but I' can't put output or coil or MB to high mode. I can set it only mannualy othervise won't work. I have also looked that output or MB in not used in no other place. Any suggestions for this problem? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted June 15, 2019 MVP 2022 Report Share Posted June 15, 2019 1. Make sure you're calling the subroutine. The fact that you bit doesn't go on with a SET coil hanging on the rail indicates the logic isn't being solved. 2. Never, ever, ever use a NO contact with a toggle coil output. The result will be a bit that chatters with every other scan. Use a positive transitional instead. Joe T. Quote Link to comment Share on other sites More sharing options...
pesi78 Posted June 16, 2019 Author Report Share Posted June 16, 2019 Thanks a lot. Quote Link to comment Share on other sites More sharing options...